Diagnosing Intermittent Shutdowns on MMG35 Generator with JD 4024TF270 Engine
#1
Overview of the MMG35 Generator and Engine Configuration
The MMG35 is a mobile diesel generator commonly deployed in remote camps, construction sites, and emergency power setups. It features a John Deere 4024TF270 electronic diesel engine, a four-cylinder turbocharged unit known for its fuel efficiency and compact footprint. This engine is electronically governed and integrated with a digital control panel that monitors oil pressure, crank cycles, temperature, and fault codes.
The generator’s control system includes a programmable logic controller (PLC), electronic fuel solenoid, oil pressure sensor, and crank cycle monitor. These components work together to ensure safe startup, continuous operation, and automatic shutdown in case of fault detection.
Symptoms of Shutdown and Startup Failure
In one field case, the generator began shutting down randomly. Sometimes it attempted to restart automatically, other times the screen went blank with no fault code. Initial shutdowns displayed low oil pressure, followed by overcrank errors. Eventually, the unit failed to start without starting fluid, suggesting a fuel delivery issue.
These symptoms point to multiple overlapping faults:
  • Low oil pressure warning may be real or sensor-related
  • Overcrank fault indicates the engine failed to start within the programmed number of attempts
  • Blank screen suggests power loss to the control panel or internal PLC fault
  • Starting fluid dependency implies delayed fuel solenoid activation or low compression
Understanding Overcrank and Fuel Delay
The overcrank error is triggered when the engine cranks but fails to reach ignition RPM within a set time. This can be caused by:
  • Weak battery voltage
  • Faulty fuel solenoid
  • Air in fuel lines
  • Low compression due to worn rings or valves
In this case, the engine only begins fueling after running for 10 seconds, which is abnormal. The fuel solenoid should activate immediately upon crank signal. Delayed fueling may be caused by:
  • Faulty solenoid coil or relay
  • PLC programming error
  • Voltage drop during crank cycle
  • Grounding issues in the control harness
Oil Pressure Sensor and Safety Shutdown
The oil pressure sensor is critical to engine protection. If it fails or reads inaccurately, the PLC will shut down the engine to prevent damage. To verify:
  • Install a mechanical oil pressure gauge and compare readings
  • Check sensor wiring for corrosion or loose terminals
  • Replace the sensor with a known-good unit if readings are erratic
If oil pressure is genuinely low, inspect the oil pump, relief valve, and filter for blockage or wear.
Blank Screen and Electrical Integrity
A blank control panel screen during shutdown suggests:
  • Internal PLC fault
  • Power supply interruption
  • Loose battery cables or ground strap
  • Failed display module
Check the main fuse block, battery terminals, and control panel connectors. If the screen remains blank after restart attempts, the PLC may need replacement or reprogramming.
Recommendations for Field Repair
To restore reliable operation:
  • Replace the fuel solenoid and verify immediate activation during crank
  • Test oil pressure with a mechanical gauge and replace sensor if needed
  • Inspect battery voltage during crank cycle; replace if voltage drops below 10V
  • Clean and tighten all ground connections
  • Check for diagnostic codes using the onboard interface or external reader
  • Reprogram or replace the PLC if screen faults persist
Conclusion
Intermittent shutdowns on the MMG35 generator with JD 4024TF270 engine are often caused by overlapping faults in fuel delivery, oil pressure sensing, and control panel logic. By systematically testing each subsystem—starting with the fuel solenoid and oil pressure sensor—technicians can isolate the root cause and restore stable operation. In remote environments like Alaskan camps, reliability is paramount, and preventive maintenance is the best defense against cascading failures.
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  Engine Rattle After Oil Ingestion in a Skid Steer MikePhua 0 70 01-06-2026, 02:43 AM
Last Post: MikePhua
  Why an Engine Won’t Shut Off MikePhua 0 113 01-04-2026, 05:54 PM
Last Post: MikePhua
  Bobcat S205 High Speed Drive Switch Intermittent MikePhua 0 198 12-30-2025, 08:46 PM
Last Post: MikePhua
  Wiring a DT466 Engine Installed in a Michigan Loader MikePhua 0 216 12-27-2025, 07:15 PM
Last Post: MikePhua
  John Deere 310C Fuel Draining Into Engine Oil MikePhua 0 222 12-25-2025, 08:39 AM
Last Post: MikePhua
  Caterpillar D8N Engine Removal MikePhua 0 299 12-15-2025, 03:56 PM
Last Post: MikePhua
  Caterpillar 3412 Engine Starting Issues MikePhua 0 319 12-15-2025, 03:55 PM
Last Post: MikePhua
  Engine Blow-By MikePhua 0 320 12-15-2025, 03:21 PM
Last Post: MikePhua
  Hough H-60B Replacement Engine MikePhua 0 335 12-15-2025, 03:13 PM
Last Post: MikePhua
  Diagnosing No-Start Issues in a 1994 Western Star 4964FX with Detroit Diesel Series 60 MikePhua 0 382 11-19-2025, 05:09 PM
Last Post: MikePhua
  315 Cat Engine Flutter — What It Is and What Might Be Causing It MikePhua 0 387 11-19-2025, 05:07 PM
Last Post: MikePhua
  Komatsu D45 Engine Damage Likely Caused by Turbo Fragment Ingestion and Requires Full Head Inspection MikePhua 0 422 11-19-2025, 04:03 PM
Last Post: MikePhua
  Loss of Power in CAT 420D Backhoe Often Linked to Throttle Linkage Wear or Engine Weakness MikePhua 0 384 11-19-2025, 03:50 PM
Last Post: MikePhua
  Slow Implement Response on Hitachi EX235 After Engine Overhaul Often Caused by Electrical Disruption or Pump Control Signal Loss MikePhua 0 411 11-19-2025, 03:44 PM
Last Post: MikePhua
  Troubleshooting Fuel Shutoff Issues on the 2000 Bobcat T200 with Deutz Engine Requires Locating the Solenoid and Verifying Power Supply MikePhua 0 391 11-19-2025, 03:42 PM
Last Post: MikePhua

Forum Jump:


Users browsing this thread: 1 Guest(s)