Diagnosing Intermittent Shutdowns on MMG35 Generator with JD 4024TF270 Engine
#1
Overview of the MMG35 Generator and Engine Configuration
The MMG35 is a mobile diesel generator commonly deployed in remote camps, construction sites, and emergency power setups. It features a John Deere 4024TF270 electronic diesel engine, a four-cylinder turbocharged unit known for its fuel efficiency and compact footprint. This engine is electronically governed and integrated with a digital control panel that monitors oil pressure, crank cycles, temperature, and fault codes.
The generator’s control system includes a programmable logic controller (PLC), electronic fuel solenoid, oil pressure sensor, and crank cycle monitor. These components work together to ensure safe startup, continuous operation, and automatic shutdown in case of fault detection.
Symptoms of Shutdown and Startup Failure
In one field case, the generator began shutting down randomly. Sometimes it attempted to restart automatically, other times the screen went blank with no fault code. Initial shutdowns displayed low oil pressure, followed by overcrank errors. Eventually, the unit failed to start without starting fluid, suggesting a fuel delivery issue.
These symptoms point to multiple overlapping faults:
  • Low oil pressure warning may be real or sensor-related
  • Overcrank fault indicates the engine failed to start within the programmed number of attempts
  • Blank screen suggests power loss to the control panel or internal PLC fault
  • Starting fluid dependency implies delayed fuel solenoid activation or low compression
Understanding Overcrank and Fuel Delay
The overcrank error is triggered when the engine cranks but fails to reach ignition RPM within a set time. This can be caused by:
  • Weak battery voltage
  • Faulty fuel solenoid
  • Air in fuel lines
  • Low compression due to worn rings or valves
In this case, the engine only begins fueling after running for 10 seconds, which is abnormal. The fuel solenoid should activate immediately upon crank signal. Delayed fueling may be caused by:
  • Faulty solenoid coil or relay
  • PLC programming error
  • Voltage drop during crank cycle
  • Grounding issues in the control harness
Oil Pressure Sensor and Safety Shutdown
The oil pressure sensor is critical to engine protection. If it fails or reads inaccurately, the PLC will shut down the engine to prevent damage. To verify:
  • Install a mechanical oil pressure gauge and compare readings
  • Check sensor wiring for corrosion or loose terminals
  • Replace the sensor with a known-good unit if readings are erratic
If oil pressure is genuinely low, inspect the oil pump, relief valve, and filter for blockage or wear.
Blank Screen and Electrical Integrity
A blank control panel screen during shutdown suggests:
  • Internal PLC fault
  • Power supply interruption
  • Loose battery cables or ground strap
  • Failed display module
Check the main fuse block, battery terminals, and control panel connectors. If the screen remains blank after restart attempts, the PLC may need replacement or reprogramming.
Recommendations for Field Repair
To restore reliable operation:
  • Replace the fuel solenoid and verify immediate activation during crank
  • Test oil pressure with a mechanical gauge and replace sensor if needed
  • Inspect battery voltage during crank cycle; replace if voltage drops below 10V
  • Clean and tighten all ground connections
  • Check for diagnostic codes using the onboard interface or external reader
  • Reprogram or replace the PLC if screen faults persist
Conclusion
Intermittent shutdowns on the MMG35 generator with JD 4024TF270 engine are often caused by overlapping faults in fuel delivery, oil pressure sensing, and control panel logic. By systematically testing each subsystem—starting with the fuel solenoid and oil pressure sensor—technicians can isolate the root cause and restore stable operation. In remote environments like Alaskan camps, reliability is paramount, and preventive maintenance is the best defense against cascading failures.
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  International TD-20B Dozer and DT-429 Engine Push Rod Replacement MikePhua 0 10 8 hours ago
Last Post: MikePhua
  Diagnosing Control Lag in the Simon 32' All-Terrain Scissor Lift MikePhua 0 13 9 hours ago
Last Post: MikePhua
  Diagnosing and Resolving Engine Knock in JCB 1550 Backhoes MikePhua 0 7 10 hours ago
Last Post: MikePhua
  Diagnosing and Resolving Crankshaft Position Sensor Issues in Caterpillar 299D MikePhua 0 7 10 hours ago
Last Post: MikePhua
  Diagnosing Brake Failure on the Komatsu D65E-7 Dozer MikePhua 0 10 10 hours ago
Last Post: MikePhua
  Case 580C Engine Detonation and Rebuild Insights MikePhua 0 5 10 hours ago
Last Post: MikePhua
  Troubleshooting a Caterpillar D5C Engine That Won't Shut Off MikePhua 0 8 10 hours ago
Last Post: MikePhua
  Can the Komatsu 507 Loader Be Upgraded with a Modern Engine MikePhua 0 6 11 hours ago
Last Post: MikePhua
  How Do You Remove Sleeves from a Case 188D Diesel Engine MikePhua 0 5 11 hours ago
Last Post: MikePhua
  Why Does the Engine Stall When Operating Hydraulics on a Halla HE280 MikePhua 0 7 10-18-2025, 08:14 PM
Last Post: MikePhua
  Troubleshooting Fuel and Engine Problems on the JCB 210S MikePhua 0 7 10-18-2025, 08:14 PM
Last Post: MikePhua
  Diagnosing Starter Failure on the International Harvester 100E MikePhua 0 3 10-18-2025, 08:05 PM
Last Post: MikePhua
  Diagnosing Hydraulic Failure on the CAT 951C Track Loader MikePhua 0 6 10-18-2025, 07:53 PM
Last Post: MikePhua
  Resolving Intermittent Wiring Issues in the 2010 CAT 252B Skid Steer MikePhua 0 6 10-18-2025, 07:52 PM
Last Post: MikePhua
  Diagnosing Oil Contamination in a Deutz BF4M1012 Engine MikePhua 0 7 10-18-2025, 07:50 PM
Last Post: MikePhua

Forum Jump:


Users browsing this thread: